I would like to put a scenario and ask you to agree, disagree, correct, comment, etc. one request don't comment just for the sake of making a comment:
a decision is needed to buy either two pumps for two different flow,head conditions (all other properties/parameters the same) or one pump and a VFD
Say the larger requirement 600 gpm x 585 ft head needs 1200 bhp, at 1500 rpm, using an impeller diameter of 24 inches.
The smaller condition is 200 gpm x 570 ft head. Since the impeller diameter needs to remain the same, otherwise there is no advantage of a VFD, the smaller condition is 200 gpm x 570 ft say 400 bhp
Since head is about the same, the speed needed for the smaller case would be 1500 x 200/600 = 500 rpm
Torque needed at 600 gpm = 63000 x 1200/1500 = 50,400 lb.inches torque needed at 200 gpm = 63000 x 400/500 = 50,400 lb.inches
Select a drive which covers this working range
Select a motor which will deliver the required torque value at both speed conditions. The one remaining thing is that amperage of the drive should be greater than the full load amps of the motor, stamped on the motor nameplate. For now disregard the motor SF.
Would a drive selected in this manner prove acceptable?
thank you
a decision is needed to buy either two pumps for two different flow,head conditions (all other properties/parameters the same) or one pump and a VFD
Say the larger requirement 600 gpm x 585 ft head needs 1200 bhp, at 1500 rpm, using an impeller diameter of 24 inches.
The smaller condition is 200 gpm x 570 ft head. Since the impeller diameter needs to remain the same, otherwise there is no advantage of a VFD, the smaller condition is 200 gpm x 570 ft say 400 bhp
Since head is about the same, the speed needed for the smaller case would be 1500 x 200/600 = 500 rpm
Torque needed at 600 gpm = 63000 x 1200/1500 = 50,400 lb.inches torque needed at 200 gpm = 63000 x 400/500 = 50,400 lb.inches
Select a drive which covers this working range
Select a motor which will deliver the required torque value at both speed conditions. The one remaining thing is that amperage of the drive should be greater than the full load amps of the motor, stamped on the motor nameplate. For now disregard the motor SF.
Would a drive selected in this manner prove acceptable?
thank you