Punching Shear in Foundations - Bending

Luceid

Structural
Feb 16, 2023
206
US
Hey all - I've got a concrete structure that we've designed using pinned-base assumptions with a mat foundation system where the columns are delivering vertical point loads at the base.

The SAFE model has a subgrade modulus spring support - so the mat foundation generates flexural moments as it deforms under loading. Many of these columns are near the edges/corners of the mat - so they often get some tricky moments in two directions which are being designed for flexurally.

When it comes to the punching shear of these columns through the raft - are the moments in the raft considered as part of the punching calculation as they are in elevated slab conditions with "restrained/fixed" slab-column collections? Or would you just take the axial load from the column and essentially check V/A - no component due to raft flexure? I have a tough time understanding the flexural component of punching shear in general - with this case I am even less sure what is clear.
 
Replies continue below

Recommended for you

I would think that you do not need to consider the moment. Similar to a spread footing loaded by a pinned column, there would be moment in the footing. We do not consider moment when doing the punching shear check in this case. For a two way slab, we would only consider moment with punching shear when a moment is transferred from the two way slab into the column.

Since no moment is in the column itself, I think no moment would be considered for the punching shear check.
 
Jumping in too late, but it is the portion of unbalanced moment transferred by shear that you design for. No moment in the pier means there is no unbalanced moment.
 