I am intending to calculate the punching shear of an edge column sitting on a slab.
Per ACI 318-14 p. 364 Table 22.6.5.2, there are three equations used to determine the 2-way shear capacity. You are to take the smallest value of these three equations and consider that to be your capacity.
In the case of a corner/edge column, I see only one of those three equations that are applicable:
Vc = (2 + alpha*d/b0)*lamda*(sqrt(f'c))*b0*d
The alpha is considering corner/edge effects. My question is this:
Is the referenced equation above the "only" equation I should use to consider my capacity, or should I still consider all three equations?
Should the perimeter (b0) be adjusted for the referenced equation, even if alpha is already accounting for the edge/corner effect?
All equations are considered, and the shear perimeter is the reduced shear perimeter.
In addition to what canwesteng stated, look also the equations for permissible stress in ACI 318-19, they have been changed.