genRman
Electrical
- Aug 3, 2001
- 27
Could anyone provide enlightenment on a problem I am facing with a Gas engine driven 11kV genset?
We have a gas engine, direct coupled (frame close coupled) to a 11kV 2/3rds pitch 3250kVA generator.
Connection is in start with a floating neutral.
Customers load lead connections are made in single steel wire armoured with the armour being connected at the switch end to ground only.
The set base frame is split in 2 halfs, one for the generator, the other for the engine. The generator base frame is connected to the common earth bus by a 50mmsq cable. There is cross earth bonding between the engine to base frame ( engine & gen on rubber AVM's), gen to base frame, engine base frame to generator base frame, engine to control panel & from control panel back to the common earth bus.
Under no load operation ( even with the load leads disconnected) we see a current flowing in the earth conductor, aproximately 6.5 to 15 amps.
Measure that with a slightly higher impeadance instrument & that value drops off quicky to somthing like 1.7A
The current is at 50Hz, & varies with the change of speed of the genset. The current amplitude varies with the change in generator terminal voltage.
There is significant stator field flux around the generator frame and a differential between drive end and non drive end of the generator in the regions of 182mV in open circuit condition.
My initial thoughts were capacitive coupling between the generator HV winding the surrounding metal, generating a potential gradient, but can't balance that against the positive current flow through so many different paths
Any bright ideas people?
We have a gas engine, direct coupled (frame close coupled) to a 11kV 2/3rds pitch 3250kVA generator.
Connection is in start with a floating neutral.
Customers load lead connections are made in single steel wire armoured with the armour being connected at the switch end to ground only.
The set base frame is split in 2 halfs, one for the generator, the other for the engine. The generator base frame is connected to the common earth bus by a 50mmsq cable. There is cross earth bonding between the engine to base frame ( engine & gen on rubber AVM's), gen to base frame, engine base frame to generator base frame, engine to control panel & from control panel back to the common earth bus.
Under no load operation ( even with the load leads disconnected) we see a current flowing in the earth conductor, aproximately 6.5 to 15 amps.
Measure that with a slightly higher impeadance instrument & that value drops off quicky to somthing like 1.7A
The current is at 50Hz, & varies with the change of speed of the genset. The current amplitude varies with the change in generator terminal voltage.
There is significant stator field flux around the generator frame and a differential between drive end and non drive end of the generator in the regions of 182mV in open circuit condition.
My initial thoughts were capacitive coupling between the generator HV winding the surrounding metal, generating a potential gradient, but can't balance that against the positive current flow through so many different paths
Any bright ideas people?