Query about meter stack

Status
Not open for further replies.

katwalatapan

Electrical
Aug 9, 2011
153
Hello,

I have a query concerning selection of compatible meter stack. The multi-unit residential facility is fed via 3-phase, 4W, 120/208V, 400A main electrical service. Each apartment unit has a 100A, 1-phase, 3W, 120/208V electrical panel and the facility has 150A, 3-phase, 4W, 120/208V house panel. Each apartment unit as well as the facility is to be separately metered for electrical consumption.

I wanted to inquire if the best way to separately meter the apartment units and house panel, is to feed the main electrical service to a 400A, 3-phase, 120/208V meter stack, where apartment units have 100/125A, 4-Jaw, combination meter socket c/w 100A, 2-Pole breaker and a 200A, 13-Jaw, combination meter socket c/w 150A, 3-Pole breaker. The line side of the meter stack would also have a 400A, 3-phase, 4W, 120/208V main disconnect switch. OR,

Would it be best to split the 400A, 3-phase, 4W, 120/208V main electrical service via splitter box into 150A, 3-phase, 4W, 120/208V for house panel and 250A, 1-phase, 3W, 120/208V for apartment units. The 150A, 3-phase could then be metered separately via single, 7-Jaw, utility meter and the 250A, 1-phase for apartment units could be measured via meter stack with individual 100A, 4-Jaw utility meter.

I'd appreciate your comments on the above scenario.

Thank you.
 
Replies continue below

Recommended for you

What does the local utility have to say? It will be their meters, it doesn't matter what anybody else says.
 
You will need at a minimum, 5 jaw meters. A single phase meter will see the 208 volts and assume that the single phase voltage is 208/2 = 104 Volts rather than the actual 120 Volts. The metering of all 120 Volt loads will be low by a factor of 104V/120V or 87%.
Been there done that.
A customer used 4 jaw meters to meter 120/208 Volt shore power sold to fishing boats. He couldn't understand why he was losing money.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Thank you very much for your responses.

I will approach the utility for their approved method. I wanted to inquire if a meter stack could have both 1-phase as well as 3-phase meter sockets installed in them OR would I have to install a splitter to separte the 1-phase and 3-phase meters.
 
Why?? 120/208 Volts is not single phase. It is two out of three phases. You can't meter 120/208 Volts with a four jaw single phase meter.
Your local utility will have standards. Meter stacks are often custom assembled and mixing meter bases should not be a problem. In any event, 120/208 Volts may be metered with a full three phase meter.
OP said:
I will approach the utility for their approved method.
That is the way to go.
I will be very surprised if you need a splitter.
The last stack I spec'ed had a mix of 100 Amp and 200 Amp meter sockets. I worked with the builder and basically spec'ed each section of the stack.
If your supplier has a problem delivering a stack with mixed bases, look for another supplier. Check the Yellow Pages for panel builders.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 