SprinklerDesigner2
Mechanical
I have a three story motel having sprinklers per NFPA 13R except the owner, and only the owner, insists the attic have sprinklers.
First two floors are non-combustible poured in place reinforced concrete with concrete block walls having metal studs and drywall. The only part of this building having combustible construction is the attic area.
As you can see not a normal sloped attic, the roof trusses gently slope to the center of the building where there are internal gutters.
Maximum depth of trusses is under 3'-0" and has drywall fastened to the underside except at the entry way and bathrooms of individual units.
I'm looking at the Viking VK900 specific application sprinkler.
What about the space with the green ??? where the depth from deck to ceiling below exceeds 3'-0"
The purple lines indicate where drywall will be fixed and as far as I can tell there isn't any drywall attched to the underside of the wood joists in the area above the bathroom or entry way.
Do I use a standard upright sprinkler in this area? If so do baffles need to be installed separating the area? I wouldn't think so but I am not sure.
IBC and it seems a very strange setup to me but I am not an architect.
First two floors are non-combustible poured in place reinforced concrete with concrete block walls having metal studs and drywall. The only part of this building having combustible construction is the attic area.
As you can see not a normal sloped attic, the roof trusses gently slope to the center of the building where there are internal gutters.
Maximum depth of trusses is under 3'-0" and has drywall fastened to the underside except at the entry way and bathrooms of individual units.
NFPA #13 - 2013 said:8.15.1.6 Sprinklers used in horizontal combustible concealed spaces (with a slope not exceeding 2 in 12) with combustible wood truss, wood joist construction, or bar joist construction having a combustible upper surface and where the depth of the space is less than 36 in. (914 mm) from deck to deck or with double wood joist construction with a maximum of 36 in. (914 mm) between the top of the bottom joist and the bottom of the upper joist shall be listed for such use.
I'm looking at the Viking VK900 specific application sprinkler.
What about the space with the green ??? where the depth from deck to ceiling below exceeds 3'-0"
The purple lines indicate where drywall will be fixed and as far as I can tell there isn't any drywall attched to the underside of the wood joists in the area above the bathroom or entry way.
Do I use a standard upright sprinkler in this area? If so do baffles need to be installed separating the area? I wouldn't think so but I am not sure.
IBC and it seems a very strange setup to me but I am not an architect.