krisys
Electrical
- May 12, 2007
- 458
We have a large oil field having a length of about 75 kms and width of about 65 kms. The oil wells are randomly distributed in the field. The central oil gathering station is located somewhere in the center of the filed. The oil will be collected from the field at the gathering station, processed and exported.
As the oil field is remote, it has no utility power supply. The entire power supply is met with the in-house power generation. So far, the major power requirement is in the gathering station and the power generated at the gathering station is connected locally.
The individual well heads need only a very small amount of power (say less than 10 kW) to keep the instruments and controls operating. So far the well head power was catered by the locally installed solar power system at individual well head locations. Of late the maintenance of these solar systems became challenging. Hence the Company has decided supply the well head station from the central oil gathering station and discard the solar system completely.
As the power required for individual stations is very small (<10kW) and the well head stations are distributed along the field, it has been decided to distribute power at 6.6 kV through the Rings. Each well head station will have one Ring Main Unit (RMU). The RMU will feed the well head station load through a small step down transformer.
Four (4) rings, with each consisting about eight (8) RMUs will be installed. The average length of each ring is about 45 kms. A dedicated 6.6kV power system has been created at the central oil gathering station to supply the well head station power. Two nos. of 1000 kVA transformers will supply the 6.6kV switchboard. The 6.6 kV Switchboard has normally closed bus tie.
As the ring cable is too long, capacitance is high and as a result, a big voltage rise is expected at the central oil gathering station 6.6 kV bus. To overcome this, two nos. of shunt reactors, rated 350 kVA each (one reactor per bus section) will be installed.
The distribution system is as indicated in the below sketch.
<img src=" border="0" alt="Image and video hosting by TinyPic">
I would like the panel to discuss the pros and cons of this distribution with respect to the following:
1) The preferred ring operation philosophy (i.e. close ring or open ring)
2) The risk of switching transient. Whether the complete ring can be energized (i.e. say a cable length of about 45 kM) from the main switchboard without risking the transient over voltage?
4) Risk of parallel resonance in the system due to variable capacitance (depends on the no. of rings and the ring sections energized)
5) In my own view instead of having the shunt rectors, the installation of 1000 kVA transformers with very high impedance (say 35%) would regulate the voltage better. Also the possible parallel resonance would be eliminated. When the ring capacitive current increases, the inductive drop proportionately through the transformer.Thus resulting in a better voltage regulation.
6) The well head station load is mainly DC UPS (battery charger). Hence a good percentage of harmonic injection is also expected. I am afraid that some of the harmonics currents might excite the circuit to give rise to the over voltage/damage to the system.
As the oil field is remote, it has no utility power supply. The entire power supply is met with the in-house power generation. So far, the major power requirement is in the gathering station and the power generated at the gathering station is connected locally.
The individual well heads need only a very small amount of power (say less than 10 kW) to keep the instruments and controls operating. So far the well head power was catered by the locally installed solar power system at individual well head locations. Of late the maintenance of these solar systems became challenging. Hence the Company has decided supply the well head station from the central oil gathering station and discard the solar system completely.
As the power required for individual stations is very small (<10kW) and the well head stations are distributed along the field, it has been decided to distribute power at 6.6 kV through the Rings. Each well head station will have one Ring Main Unit (RMU). The RMU will feed the well head station load through a small step down transformer.
Four (4) rings, with each consisting about eight (8) RMUs will be installed. The average length of each ring is about 45 kms. A dedicated 6.6kV power system has been created at the central oil gathering station to supply the well head station power. Two nos. of 1000 kVA transformers will supply the 6.6kV switchboard. The 6.6 kV Switchboard has normally closed bus tie.
As the ring cable is too long, capacitance is high and as a result, a big voltage rise is expected at the central oil gathering station 6.6 kV bus. To overcome this, two nos. of shunt reactors, rated 350 kVA each (one reactor per bus section) will be installed.
The distribution system is as indicated in the below sketch.
<img src=" border="0" alt="Image and video hosting by TinyPic">
I would like the panel to discuss the pros and cons of this distribution with respect to the following:
1) The preferred ring operation philosophy (i.e. close ring or open ring)
2) The risk of switching transient. Whether the complete ring can be energized (i.e. say a cable length of about 45 kM) from the main switchboard without risking the transient over voltage?
4) Risk of parallel resonance in the system due to variable capacitance (depends on the no. of rings and the ring sections energized)
5) In my own view instead of having the shunt rectors, the installation of 1000 kVA transformers with very high impedance (say 35%) would regulate the voltage better. Also the possible parallel resonance would be eliminated. When the ring capacitive current increases, the inductive drop proportionately through the transformer.Thus resulting in a better voltage regulation.
6) The well head station load is mainly DC UPS (battery charger). Hence a good percentage of harmonic injection is also expected. I am afraid that some of the harmonics currents might excite the circuit to give rise to the over voltage/damage to the system.