question on pvc pipe in fire system according to nfpa

Status
Not open for further replies.

rouid

Mechanical
May 10, 2004
1
dear sir,
i have fire system under ground, outside bulinding are there restrication to use pvc pipe according to nfpa
 
Replies continue below

Recommended for you

If you are talking underground piping, all you need is pvc piping that is listed for fire protection use. Make sure you are using piping with the appropriate pressure ratings for the working pressure of the system. Additionally, when using pvc piping with slip joints, the thrust blocks are very important to keep the piping from "blowing out" during testing.
 
If it is listed pipe and is designed correctly NFPA has no problem with it.
 