smoradm
Civil/Environmental
- Oct 26, 2012
- 1
A pump is proposed for storm water detention. The specs calls for a Duplex, 4" force main, 363 GPM, 6' TDH. The motor size is 020-2.0 HP and Power Characteristics is43 - 460V/3PH/60Hz.
The reviewing agency has provided the following comments:
Comment 1: A back up pump is required in event of pump failure.
My Question: The pump is already a Duplex pump. Isn't this considered a back up pump?
Comment 2: Provide emergency power from a second source or install a quick connect for mobile generator.
My question: I am not designing the electric panel or connection. Will a NOTE on the pump detail drawing such as: " Contractor to provide an emergency power from a second source or install a quick connect for a mobile generator." acceptable or usually done by civil engineer.
Thanks
The reviewing agency has provided the following comments:
Comment 1: A back up pump is required in event of pump failure.
My Question: The pump is already a Duplex pump. Isn't this considered a back up pump?
Comment 2: Provide emergency power from a second source or install a quick connect for mobile generator.
My question: I am not designing the electric panel or connection. Will a NOTE on the pump detail drawing such as: " Contractor to provide an emergency power from a second source or install a quick connect for a mobile generator." acceptable or usually done by civil engineer.