SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
Last time I had a project dealing with sprinklers in attics was before the AP sprinkler made it's appearance.
Application: The Use of Specific Application Sprinklers for Protecting Attics
Tyco did a pretty good job laying out the details except for a few areas where I am still a little confused and looking for confirmation.
Question #1: I'm 99% sure I understand what direction the measurement of "12 feet perpendicular to slope" is but not 100% sure. Do I have the 10' and 12' maximum dimensions correctly aligned with the slopes? Generally I am pretty good at visualizing things but on this one I've developed a mental block or something.
Question #2: I know what stagger is but is it defined? On FIG. 7J - CALCULATION 1 the AP sprinklers in the hip are supposed to be staggered but aren't.
Question #3: Is there a minimum distance between AP sprinklers when AP sprinklers are on different planes of the hip? I wish Tyco included samples with some actual dimensions.
Question #4: So many of their figures indicate AP sprinklers throughout the hip but then some indicate SD sprinklers on one side of the hip which which I feel is the only way to go with this type of cut down roof truss. Can you think of a construction where AP sprinklers would be called for on both sides of the ridge line in lieu of SD sprinklers on one side when utilizing cut down trusses?
On the patent Combustible concealed space sprinkler system and method
They seem to be indicating a line of sprinklers very close to the ridge on one side?
Application: The Use of Specific Application Sprinklers for Protecting Attics
Tyco did a pretty good job laying out the details except for a few areas where I am still a little confused and looking for confirmation.
Question #1: I'm 99% sure I understand what direction the measurement of "12 feet perpendicular to slope" is but not 100% sure. Do I have the 10' and 12' maximum dimensions correctly aligned with the slopes? Generally I am pretty good at visualizing things but on this one I've developed a mental block or something.
Question #2: I know what stagger is but is it defined? On FIG. 7J - CALCULATION 1 the AP sprinklers in the hip are supposed to be staggered but aren't.
Question #3: Is there a minimum distance between AP sprinklers when AP sprinklers are on different planes of the hip? I wish Tyco included samples with some actual dimensions.
Question #4: So many of their figures indicate AP sprinklers throughout the hip but then some indicate SD sprinklers on one side of the hip which which I feel is the only way to go with this type of cut down roof truss. Can you think of a construction where AP sprinklers would be called for on both sides of the ridge line in lieu of SD sprinklers on one side when utilizing cut down trusses?
On the patent Combustible concealed space sprinkler system and method
They seem to be indicating a line of sprinklers very close to the ridge on one side?