Hello all

I have questions:
1- is it a good idea to use a perforated spiral duct into an ofice space
2- any rul of thumb to select a water pump for a boiler

Thanks
 
Replies continue below

Recommended for you

1. Not really. Likely to get hot and cold spots as the duct dumps in the space.
2. Use the boiler output and your desired delta T to pick flow. Use the boiler catalogue to determine head loss... not really a rule of thumb, that's actually what you do.
 
My rule-of-thumb: I always rough-in between 7 and 13, then pick my units to match the detail design calculations.

 
I have two question; what will be the purpose of the water pump and what type of a boiler (process steam, heating steam or hot water)is it?
 