"Loud Bang" heard during occupancy

Status
Not open for further replies.

SteelPE

Structural
Mar 9, 2006
2,759
I was called to one a job today because a client heard a “loud bang” during occupancy of the building (which took place this weekend). This happened once on Thursday and again on Saturday in the same general area. During the site visit (which included a close inspection of the connections and suspended slab) I could see no sign of distress in the building. In talking to the people who heard the noise they said it sounded like someone “hit the steel with a hammer”.

Construction:

Bay 24’-0” by 28’-0”
Secondary beams W16x26 24’-0” long spaced 8’-0” o.c.
Girders W24x55 with 28 studs 28’-0” long

Slab construction
6” slab placed atop 2” 20 ga. Composite decking reinforced with 6x6 W2.1xW2.1 wwf.

The facility is a car dealership and they were basically moving cars around on the suspended floor when they heard the noise.

I have some theories on what it could possibly be but I am wondering if anyone has any ideas on what may have caused this noise.
 
Replies continue below

Recommended for you

SteelPE,
If you are a member of AISC, you can search their journal articles for "banging bolts" you can find a lot of research into this occurrence. I've read a little about it, seems kind of interesting.
It might not apply to your building, but it could be a start in the right direction.

Let us know what it is, if you ever find it.

Hope this helps.

RC
All that is necessary for the triumph of evil is that good men do nothing.
Edmund Burke

 
RCraine has it... sounds like a "banging bolts" occurence.
 
Thank you RCrain and JKStruct. That is what my initial thought was. I have read the papers and questions in MSC. It just looks like there is really no way to prove this is what is happening? I just want to make sure this isn’t something I am overlooking.
 
I also suspect it is "banging bolts".

What type of connections are they using for the gravity beams? Bearing or Slip Critical? Were the beam and the connection parts primed or masked off? What type of bolts (TC or regular) were used and were they partially of fully torqued?
 
Jike

For the W16x26 they are using single sided angle connections. This was not my preferred connection but they worked for the light loads and made erection much easier.

The bolts are designed to be in bearing.

They applied 4 bolts per connection.

All connections are bolted – bolted.

The angles were attached to the girder in the shop.

I believe that the surface between the girder and the angle is unpainted. The surface between the secondary beam and the angle is painted.

I believed they used t.c. bolts that are fully torqued by evidence of shear spline removal.

As for the girder, they are double angle connections with 7 bolts in double shear (14 bolts to the column).
 
The typical cause for banging bolts are bolts that were designed as bearing bolts, but tightened as slip critical bolts onto an prepared fraying surface (i.e. painted surface). Your secondary beams are probably sliding into bearing and creating that noise.
 
Sounds like bolt banging to me. Not really much you can do except document it and forward it on to the incompetent erector. There's no excuses for bolt banging. Typically its due to drift pins being left in too long while the connection bolts are tightened.
 
Banging sounds means may be web of beam is banging on bolt shanks. This additional impact load is considered or connection can break? It’s may also fall into fatigue criteria?
 