CT's were connected in delta to align the currents of a differential with those of the other side of the transformer, and to filter out zero sequence current.
Normally used on the wye side of a delta-wye transformer.
New relays can make this alignment, and filter out zero sequence internally.
Some types of metering also use delta connected metering, with the assumption that there is no single phase loading.