Let me first describe the application:
35kv shielded cable, direct buried approx 1km, 6-1C-500MCM. Line differential relays are 3 element, dual fiber channel, with integrated overcurrent and distance protection. My system has a fault level of about 20KA symetrical, and the system is resistively grounded with two sources of ground fault current on the system rated at 400A each. At one end of the line I only have 1 phase - phase PT. The line differential relays are using 1200/5A CT's and the pickup is .2pu, or 240A, and also has a 50/5A ZSCT at each end, connected to the ground current input of the relay.
My problem is I would like to increase the sensitivity of 87 relay for in zone ground faults to decrease damage to the cable for a cable fault, but the relay only compares the three individual phase currents, and not the ground current input. One of my two ground fault current sources is a signifigant distance from the cable installation (10km) so the amount ground current it would supply is reduced.
The "weird" idea I had was to use one of the phase inputs of the relays for the ZSCT's to provide me with 87P and 87G protection. Phase would be connected to the ZSCT at each end, and phase B & C CT's would be tied to their respective phase current inputs at each end. I would then have diff protection for in zone ground faults, and diff protection for any possible 2 or 3 phase faults. I've calculated the charging current at 7A, so that shouldn't be an issue. I would then increase the pick up from .2pu to .5pu so my 87G setting would 25A, and my 87P would be 600A. I'm not using overcurrent or distance protection in the relay.
Can any body think of any potential pitfalls with this arrangement? (I realize the reading's for the ground current would be off because the ratio is entered at 1200/5A, but I don't think this will be an issue.)
Also I used 6*charging current for my calculation for 6 conductor, should I have?
Thank You,
Gord
35kv shielded cable, direct buried approx 1km, 6-1C-500MCM. Line differential relays are 3 element, dual fiber channel, with integrated overcurrent and distance protection. My system has a fault level of about 20KA symetrical, and the system is resistively grounded with two sources of ground fault current on the system rated at 400A each. At one end of the line I only have 1 phase - phase PT. The line differential relays are using 1200/5A CT's and the pickup is .2pu, or 240A, and also has a 50/5A ZSCT at each end, connected to the ground current input of the relay.
My problem is I would like to increase the sensitivity of 87 relay for in zone ground faults to decrease damage to the cable for a cable fault, but the relay only compares the three individual phase currents, and not the ground current input. One of my two ground fault current sources is a signifigant distance from the cable installation (10km) so the amount ground current it would supply is reduced.
The "weird" idea I had was to use one of the phase inputs of the relays for the ZSCT's to provide me with 87P and 87G protection. Phase would be connected to the ZSCT at each end, and phase B & C CT's would be tied to their respective phase current inputs at each end. I would then have diff protection for in zone ground faults, and diff protection for any possible 2 or 3 phase faults. I've calculated the charging current at 7A, so that shouldn't be an issue. I would then increase the pick up from .2pu to .5pu so my 87G setting would 25A, and my 87P would be 600A. I'm not using overcurrent or distance protection in the relay.
Can any body think of any potential pitfalls with this arrangement? (I realize the reading's for the ground current would be off because the ratio is entered at 1200/5A, but I don't think this will be an issue.)
Also I used 6*charging current for my calculation for 6 conductor, should I have?
Thank You,
Gord