Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Rack storage area covered by the rack system

Status
Not open for further replies.

SprinklerDesigner2

Mechanical
Nov 30, 2006
1,251
I know I have seen it.

130,000 sq. ft. building with rack storage of class IV commodity to 25' high.

Four overhead systems are required.

Rack sprinklers are required with one level of sprinklers in each rack. ESFR on this one is out of the question.

I know it's in the standards somewhere but where does it say the area covered by my in rack system must:

1) be below the overhead and

2) not exceed 40,000 sq. ft?

Where does it say I can't have a single rack system cover all the racks?
 
Replies continue below

Recommended for you

NFPA 13 2010 8.13.1 System Size

The area protected by a single system of sprinklers in racks shall not exceed 40,000 sq. ft of floor area occupied by the racks, including aisles, regardless of the number of levels of in rack sprinklers.
 
Not 100% sure what you mean by "be below the overhead"

but, NFPA 13 2010 16.2.4.1.4 In rack sprinklers at one level only for storage up to and including 25 ft high shall be located at the first tier level at or above one half of the storage height.
 
I was looking for NFPA 13 2010 8.13.1 System Size. I knew it was in there but couldn't find it and needed an answer fast. :)
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor