fastline12
Aerospace
- Jan 27, 2011
- 306
Trying to design the tubing network for a slab on grade. The way I am calculating things is heat loss for all walls and roof, excluding the floor. Then I calculate the BTUs required for the space and start getting a general idea of how much water and dT I will need.
It looks like my worst case heat loss is 85,000btu, and mean will be about 40,000btu. The slab is 6000sf. I am new to calculating for radiant but the way I am looking at this is tubing ends up at he bottom of the slab at a certain temp and the soil at a certain temp. For this example, I will go with 80F target slab temp, soil temp is 50F, target indoor temp is 60F. I am trying to determine slab insulation. I do not want to over size that due to costs.
I am considering the U value of the foam BUT what I am trying to account for is the heating of the soil under the insulation. Once heat starts moving to the soil, the soil temp will rise, this reducing the btu losses? Or should I just calculate as an infinite heat sink at 50F?
I am considering the btu gain in the space by simply comparing indoor air temps vs slab temp... IE, slab at 80F, indoor at 60F, 6000sf*20F = 120k btu?
The things that stand out to me is the edges of the concrete should be insulated as there is good qty of heat loss there. As well, it seem that the hotter I push the concrete temp, the more btu loss I will have to earth so I need to balance the slab temp with demand.
As well, I am trying to determine how the flywheel effect will work for overnight swings and how to handle concerns of overheating in the space? IE, heat loss will vary through the day. Will a radiant slab be responsive enough to modulate the btu output to demand?
Heating degree days in my area are about 4700. I am considering 1" of XPS insulation, plus 2ft vertical perimeter insulation. ?
I realize there will be some variables in water temps and slab temp but I am trying to learn what standards to shoot for to get good efficiency. What kind of dTs do I need through the tubing?
It looks like my worst case heat loss is 85,000btu, and mean will be about 40,000btu. The slab is 6000sf. I am new to calculating for radiant but the way I am looking at this is tubing ends up at he bottom of the slab at a certain temp and the soil at a certain temp. For this example, I will go with 80F target slab temp, soil temp is 50F, target indoor temp is 60F. I am trying to determine slab insulation. I do not want to over size that due to costs.
I am considering the U value of the foam BUT what I am trying to account for is the heating of the soil under the insulation. Once heat starts moving to the soil, the soil temp will rise, this reducing the btu losses? Or should I just calculate as an infinite heat sink at 50F?
I am considering the btu gain in the space by simply comparing indoor air temps vs slab temp... IE, slab at 80F, indoor at 60F, 6000sf*20F = 120k btu?
The things that stand out to me is the edges of the concrete should be insulated as there is good qty of heat loss there. As well, it seem that the hotter I push the concrete temp, the more btu loss I will have to earth so I need to balance the slab temp with demand.
As well, I am trying to determine how the flywheel effect will work for overnight swings and how to handle concerns of overheating in the space? IE, heat loss will vary through the day. Will a radiant slab be responsive enough to modulate the btu output to demand?
Heating degree days in my area are about 4700. I am considering 1" of XPS insulation, plus 2ft vertical perimeter insulation. ?
I realize there will be some variables in water temps and slab temp but I am trying to learn what standards to shoot for to get good efficiency. What kind of dTs do I need through the tubing?