itsmoked
Electrical
- Feb 18, 2005
- 19,114
Situation:
108Hp Turbocharged 4cyl Cummins, approx 108hp.
Nameplate:
55.0kW
68.8kVA
240V 3-Phase
Generator is underslung on a railcar.
It is mounted in an enclosure with a protection circuit breaker.
This circuit breaker originally was a thermal/magnetic 150A 3Ph
breaker. It's relatively large:
8" high, 6"wide, 4"deep; handle 2" long, 1" wide, 1/2" thick.
Making me speculate it's a 600V breaker.
Anyway, it regularly tripped. This required the train to stop so someone could reset it. <big frown>
Someone changed it to a 200A breaker. Now it nuisance trips whenever the car is running in high ambients; 105+.
This breaker, as mentioned, is in the enclosure with the turbocharged diesel, its turbo, its radiator, and the exhaust manifold.
Questions:
1) Why is the factory breaker on this 55kW generator 150A?
Isn't 55kW/240 = 230A?
Isn't 230A/3phases = 76A?
2) Can this scheme ever be made to work based on a breaker in an weather ambient that swings regularly from -30F to 120F meaning the breaker ambient probably swings from 70F to 300F?
3) Any suggestions?
108Hp Turbocharged 4cyl Cummins, approx 108hp.
Nameplate:
55.0kW
68.8kVA
240V 3-Phase
Generator is underslung on a railcar.
It is mounted in an enclosure with a protection circuit breaker.
This circuit breaker originally was a thermal/magnetic 150A 3Ph
breaker. It's relatively large:
8" high, 6"wide, 4"deep; handle 2" long, 1" wide, 1/2" thick.
Making me speculate it's a 600V breaker.
Anyway, it regularly tripped. This required the train to stop so someone could reset it. <big frown>
Someone changed it to a 200A breaker. Now it nuisance trips whenever the car is running in high ambients; 105+.
This breaker, as mentioned, is in the enclosure with the turbocharged diesel, its turbo, its radiator, and the exhaust manifold.
Questions:
1) Why is the factory breaker on this 55kW generator 150A?
Isn't 55kW/240 = 230A?
Isn't 230A/3phases = 76A?
2) Can this scheme ever be made to work based on a breaker in an weather ambient that swings regularly from -30F to 120F meaning the breaker ambient probably swings from 70F to 300F?
3) Any suggestions?