Hello,

I am designing the grounding grid for high-speed railway substations and autotransformers (-27,5 kV and +27,5 kV) and I have not been able to find any good references for short-circuit calculations. I need to calculate the phase to earth short-circuit both in substations and in autotransformers, and also the part of that fault which returns.

Could anyone provide me references for this type of calculations, please?

Thanks.
 
Replies continue below

Recommended for you

Chapter 20 of the Areva NPAG "Protection of AC Electrified Railways" may be of use.
ftp://ftp.areva-td.com/NPAG/Chap20-352-369.pdf

Regards
Marmite
 
For some reason that link I posted doesn't work when cut & pasted. You can get to it from and search for railway. It will appear in the results and opens up fine.

Regards
Marmite
 
AREVA changed the way of downloading from their web-site. It is free again, but they require filling-up of Contact Form. If you like, proceed this way. If not - I have NRAG and as it was available for free download, I don't think it will be a violation of copyrights to post the railway section here:


------------------------
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant
 
 http://files.engineering.com/getfile.aspx?folder=924eca57-db47-4bfe-95be-b9737271f272&file=20-Protection_of_AC_elec_rail.pdf
Thank you,

I already read AREVA guide before asking. A good reference mainly for protection issues. But it was not very helpful with short-circuit calculation.
 
Another question:

In EN 50122-1 there is data for the rail conductivity: from 0,4 Siemens/km to 1,7 Siemens/km. When calculating the different return paths of a ground fault, how can be determined the part which returns from the rails? How much distance must be considered?
 