Would someone be kind enough to give me a link to allowable current loads for power cables. I need to check for 240 volt 1Ph 5.8 kW.

Thanks
 
Replies continue below

Recommended for you

Although the question sounds very simple, it does not have a "One size fits all" answer.
You must check your local codes.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
amps = 5.8 kw/.24 = 24 amps. Check the NEC table 310.16 for
cable ampacity. On the surface #10 thhn would do the job but you have not give all the info required to make the decision.
 
wareagle, but he didn't even say where in the world he is; maybe #10 and/or thhn has no relevance. If only people would ask full, complete, questions.
 
I'm thinking free air vs. direct burial, full rating vs derated for multiple conductors, 60 deg. vs 90 deg. Oh, any high ambient conditions? 100% loading or 80% loading?
Like David said!

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
It was only 2m run in air from the switch board so used 4mm2.

Thanks again.
 