Powerykh
Electrical
- May 29, 2007
- 22
Hello all, I am from IEC world. We have a 275/13.8 kV 3 phase transformer. Vector group is YNd1. There is a 4700/5A bushing CT installed at low voltage b phase. Attached is the detail of this Tx.
As the bushing CT primary side is not accessible, I can think of two option (other than the automatic test set like omicron ct analyser) to carry out the ratio check for this bushing CT:
1. Ratio to be carried our during transformer is on load
2. Injecting 3 phase low voltage (415V) to Tx HV side phase terminal (A6, B6, C6), and shorted at Tx LV side (a2, b2 , c2)
Calculation for short circuit current found at TX LV side:
Assuming tap 5 in use: 275/13.8kV, and % impedance is 11%.
HV side full load current: 235A
HV side impedance= HV side voltage/HV side Full load current=275000/235=1170 ohms
HV side impedance/phase = HV side impedance*% impedance=1170*11%=128.7ohms
HV side current/phase=Injecting voltage/HV side impedance/phase = 415/128.7=3.224A
Transformer ratio = 275000/13800=19.92
LV side current = 19.92*3.224A=64.2A
CT ratio = 4700/5=940
CT secondary current measured when 64.2A flowing in CT primary side= 64.2/940=0.068A
The secondary current measured is only around 68mA. Would like to know whether got other method to carry out this ratio test?
As the bushing CT primary side is not accessible, I can think of two option (other than the automatic test set like omicron ct analyser) to carry out the ratio check for this bushing CT:
1. Ratio to be carried our during transformer is on load
2. Injecting 3 phase low voltage (415V) to Tx HV side phase terminal (A6, B6, C6), and shorted at Tx LV side (a2, b2 , c2)
Calculation for short circuit current found at TX LV side:
Assuming tap 5 in use: 275/13.8kV, and % impedance is 11%.
HV side full load current: 235A
HV side impedance= HV side voltage/HV side Full load current=275000/235=1170 ohms
HV side impedance/phase = HV side impedance*% impedance=1170*11%=128.7ohms
HV side current/phase=Injecting voltage/HV side impedance/phase = 415/128.7=3.224A
Transformer ratio = 275000/13800=19.92
LV side current = 19.92*3.224A=64.2A
CT ratio = 4700/5=940
CT secondary current measured when 64.2A flowing in CT primary side= 64.2/940=0.068A
The secondary current measured is only around 68mA. Would like to know whether got other method to carry out this ratio test?