Hello all, I am from IEC world. We have a 275/13.8 kV 3 phase transformer. Vector group is YNd1. There is a 4700/5A bushing CT installed at low voltage b phase. Attached is the detail of this Tx.
As the bushing CT primary side is not accessible, I can think of two option (other than the automatic test set like omicron ct analyser) to carry out the ratio check for this bushing CT:
1. Ratio to be carried our during transformer is on load
2. Injecting 3 phase low voltage (415V) to Tx HV side phase terminal (A6, B6, C6), and shorted at Tx LV side (a2, b2 , c2)
Calculation for short circuit current found at TX LV side:
Assuming tap 5 in use: 275/13.8kV, and % impedance is 11%.
HV side full load current: 235A
HV side impedance= HV side voltage/HV side Full load current=275000/235=1170 ohms
HV side impedance/phase = HV side impedance*% impedance=1170*11%=128.7ohms
HV side current/phase=Injecting voltage/HV side impedance/phase = 415/128.7=3.224A
Transformer ratio = 275000/13800=19.92
LV side current = 19.92*3.224A=64.2A
CT ratio = 4700/5=940
CT secondary current measured when 64.2A flowing in CT primary side= 64.2/940=0.068A
The secondary current measured is only around 68mA. Would like to know whether got other method to carry out this ratio test?