llocou
Structural
- Mar 19, 2014
- 6
I'm looking at a concrete upstand that I've been treating as a wall. It's about 1100mm tall, 200mm thick, and there are some openings of 1050x220 mm. Some of the openings are very close to a wall edge - leaving around 115mm of concrete from edge of opening to edge of wall. How would you go about detailing this? The 'standard' practice of proving half of the bars that have been broken on either side of the opening is a bit unrealistic (the wall has 2 layers of 16mm bars @ 150mm centres both ways, so would mean fitting in 2 layers of 4 bars into the 115mm). On top of this, 14.3.7 of ACI 318 dictates that two additional 16mm bars are required around the opening in a wall with 2 layers of reinforcement. On top of this there's the good practice of providing diagonal bars, but being so close to the edge of the wall means there's no space for a diagonal bar, and simply bending it to be vertical would be an additional vertical bar on top of all the vertical bars I've already mentioned! I don't know if I'm overthinking this for a 'wall' that's so short, and isn't carrying any significant load above it. Any views would be appreciated, thanks.