RCC Column with inserted steel flats

Status
Not open for further replies.

struct4me

Civil/Environmental
Feb 4, 2013
32
Dear forum members,

What I know Steel flats plates (say size of 60mn x 5 mm) are used as earth mat in substation foundation with a spacing in both direction,but what I don't know if it is wise to take through the intersecting RCC column (between the inner set of vertical reinforcement) and then casting the upper portion of column. The intersecting side of column 450mm and other side is 400mm.
Does it beneficial as suggested by the site electrical engg or does it harm my column in long run.
Yours advise/suggestion will be well appreciated.

Regards

Rajarshi
 
Replies continue below

Recommended for you

This doesn't sound like a big deal to me so long as you're confident that you can get whatever shear capacity you require in the column where the plates will be located. The plates should also have adequate concrete cover.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.
 
Looking for any suggestion after uploading the pic.