oceanview
Marine/Ocean
- Aug 4, 2008
- 5
I am a marine engineer working onboard a smaller vessel struggling with RCCBs tripping on two of the distribution boxes. Electrical equipment is not my specialty so I am hoping for some guidance and help.
We are currently connected to a shore power supply of 380 Volts, 50 hz. This is fed through an isolation transformer and then to the main switchboard. From here through 3 pole breakers several distribution boards are supplied. Each distribution board is connected to the neutral bar on the switchboard as well as the ground bar on the switchboard.
On two of the distribution boxes the RCCBs trip immediately when any load is run through the RCCB. In other words, if I open all of the breakers supplied by the RCCB, it will latch closed. As soon as I close any of the breakers, whether it be lights, an air handler, or a stove, the RCCB trips. I can close a socket breaker and the RCCB will stay closed until I plug something into the socket (such as a light) and the RCCB immediately trips. Both of the boards began doing this at the same time.
I have tried disconnecting the neutral cable in the swithcboard to the RCCB and megger testing to ground to see if it has been damaged, but it is fine.
I have shut off everything on the entire vessel and only supplied power to the distribution board and the same thing happens.
Three other boards fitted with RCCBs are functioning fine and take the supply from the same bus bars in the switchboard and their neutrals are also on the same bar.
Any ideas?
I read from a previous post that RCCBs should only detect faults further down stream. Which means the problem should be in the distribution boards themselves. Normally, the typical process for troubleshooting something like this is to switch off all of the breakers on the distribution board and then switch them on one by one to find which one is the source of the problem. But all of them trip...
We are currently connected to a shore power supply of 380 Volts, 50 hz. This is fed through an isolation transformer and then to the main switchboard. From here through 3 pole breakers several distribution boards are supplied. Each distribution board is connected to the neutral bar on the switchboard as well as the ground bar on the switchboard.
On two of the distribution boxes the RCCBs trip immediately when any load is run through the RCCB. In other words, if I open all of the breakers supplied by the RCCB, it will latch closed. As soon as I close any of the breakers, whether it be lights, an air handler, or a stove, the RCCB trips. I can close a socket breaker and the RCCB will stay closed until I plug something into the socket (such as a light) and the RCCB immediately trips. Both of the boards began doing this at the same time.
I have tried disconnecting the neutral cable in the swithcboard to the RCCB and megger testing to ground to see if it has been damaged, but it is fine.
I have shut off everything on the entire vessel and only supplied power to the distribution board and the same thing happens.
Three other boards fitted with RCCBs are functioning fine and take the supply from the same bus bars in the switchboard and their neutrals are also on the same bar.
Any ideas?
I read from a previous post that RCCBs should only detect faults further down stream. Which means the problem should be in the distribution boards themselves. Normally, the typical process for troubleshooting something like this is to switch off all of the breakers on the distribution board and then switch them on one by one to find which one is the source of the problem. But all of them trip...