Hi
I have been working in a place that has had to reduce its power consumption from the grid until it can be upgraded. We have therefore installed a 100A generator on site, we have connected the lighting circuits and one machine to the generator supply. For the Regs we have installed a 300mA RCD on the supply for earth protection.
The machine in question has two servo drives (Inverters) fitted which instantly trip the RCD when poewered up. As I know the RFI Filters which are on the inverter supply can cause this I have removed them from the circuit and we installed a new RCD that gives 195msec delay before tripping.
Now the RCD stands when one of the inverters is switched on but trips when the second is switched in. It doesn't matter which inverter is switched first, the RCD always trips on the second.
The manufacturers of the inverters documentation state that a Type B RCD should be installed and not a AC or A type, the manufacturer of the RCD say that there is no such thing as a B type!.
I am guessing that the charging of the capacitors inside the inverters is pulling the RCD out as if the trip is reset 3 or 4 times in succesion the system stays on.
If anybody has experience in this area, any help would be gratefully recieved.
Regards
Alan Edwards
I have been working in a place that has had to reduce its power consumption from the grid until it can be upgraded. We have therefore installed a 100A generator on site, we have connected the lighting circuits and one machine to the generator supply. For the Regs we have installed a 300mA RCD on the supply for earth protection.
The machine in question has two servo drives (Inverters) fitted which instantly trip the RCD when poewered up. As I know the RFI Filters which are on the inverter supply can cause this I have removed them from the circuit and we installed a new RCD that gives 195msec delay before tripping.
Now the RCD stands when one of the inverters is switched on but trips when the second is switched in. It doesn't matter which inverter is switched first, the RCD always trips on the second.
The manufacturers of the inverters documentation state that a Type B RCD should be installed and not a AC or A type, the manufacturer of the RCD say that there is no such thing as a B type!.
I am guessing that the charging of the capacitors inside the inverters is pulling the RCD out as if the trip is reset 3 or 4 times in succesion the system stays on.
If anybody has experience in this area, any help would be gratefully recieved.
Regards
Alan Edwards