I need some help in determining whether or not to re-commission a transformer or not, has we are not 100% sure that the transformer had or had not seen a through fault. The transformer feeder did not trip but the incomer to that board did trip on Timed- earth fault(51G), no other protection on that transformer did pick up, ie transformer diff. on the day of the assumed fault we did megger all 3 phases with the red phase going straight down to earth, but the blue and white giving me 2.3 M ohms of 5kv, but this to me is incorrect has the transformer is a Delta/star and I Meggered the delta side. The following day I deiced that I will do a ratio test, sensitive resistance test and Hi-potential test. But to my surprise the transformer came out clean. Even when re-meggered the values were 21 M ohm between all phases and earth. But from DGA I found high levels of Acetylene ( 89 ppm) and that shows the transformer is not operational. Can I get some other advice. I have already taken the transformer out and sent it for refurbishment.