Hello. I am in need of some advice on an issue we are having with two of three Caterpillar 250Kw units that are paralleled to supply a stand alone floating maintenance barge. The condition we are experiencing is that units #one and #two together run well and share the load equally and power factors adjust well. When you parallel either #one or #two with #three individually the power factors do not react well and the loads are not shared equally. We have surmised that it is cross current based on the bus amperage and individual unit amperage gages comparisons. And the fact that the power factor meters lag and lead respectively.
As I read through some of the threads, which were very helpful, I have some questions.
The gensets are SR4 CATS with upfitted VR6 regulators. We have had the Cat techs in to work on the system. They tuned in the 2301a controls and got the units to share pretty well. But, told us based on the age of the equipment that the power factors are as good as it gets.
Finally,
Question one: Can anyone tell me if the burdeon resistor is internal to the VR6?
Question two: How can you tell if the polarity of the CTs are correct?
I suspect that the polarity of the CT on unit #three is not correct but am leary of reversing it without some more information.
Sorry this got so long. Wanted everyone to have as much info as possible
Hello. I am in need of some advice on an issue we are having with two of three Caterpillar 250Kw units that are paralleled to supply a stand alone floating maintenance barge. The condition we are experiencing is that units #one and #two together run well and share the load equally and power factors adjust well. When you parallel either #one or #two with #three individually the power factors do not react well and the loads are not shared equally. We have surmised that it is cross current based on the bus amperage and individual unit amperage gages comparisons. And the fact that the power factor meters lag and lead respectively.
As I read through some of the threads, which were very helpful, I have some questions.
The gensets are SR4 CATS with upfitted VR6 regulators. We have had the Cat techs in to work on the system. They tuned in the 2301a controls and got the units to share pretty well. But, told us based on the age of the equipment that the power factors are as good as it gets.
Finally,
Question one: Can anyone tell me if the burdeon resistor is internal to the VR6?
Question two: How can you tell if the polarity of the CTs are correct?
I suspect that the polarity of the CT on unit #three is not correct but am leary of reversing it without some more information.
Sorry this got so long. Wanted everyone to have as much info as possible