Ready to close contacts on ACB/MCCBs

Status
Not open for further replies.

GAZ4333

Electrical
Oct 20, 2009
4
Guys,

I have been looking around on the internet for a description of the operation and workings of a ready to close contact on ACBs & MCCBs, can any of you clever people explain the workings to me please.

Regards

Gaz
 
Replies continue below

Recommended for you

On an ACB it would usually be combination of functions to indicate that springs were charged, interlocks were free, no standing trip commands, etc. On an MCCB with an energy-storing actuator it would be a similar set of conditions. On a standard MCCB I'm not sure, because they are manual devices.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Never heard of it. Traditionally, there is a green light to indicate the breaker is open and this light is powered from the closing circuit. So if the green light is on, it should be ready to close, or the breaker is broken. I suppose a limit switch contact from the charged spring could be used as a more positive indication, but I've never seen it done.
 