Curious how other people handle setting up development length/splice length tables on their drawings. To set up useful tables requires building in some assumptions, for example:
- Assuming you use ACI 12.2.2 simplified equations there are requirements for clear spacing, min. clear cover, and ties/no ties.
- If you are making a table for interior elevated slabs you would normally be using 0.75" cover, do you therefore build into your table a change in equations after #6 bars, i.e. when the cover of 0.75" becomes smaller than 1 db?
- Similar questions for walls: at basement walls we show the vertical reinforcing as the outer curtain, but on shearwalls we show it inside the the horizontals - do you create two tables and account for the different typical covers for those two situations and then build that into your table? There is also the issue that portions of shearwalls may be tied/confined bars while others are not, this also may impact the development length.
- Assuming you use ACI 12.2.2 simplified equations there are requirements for clear spacing, min. clear cover, and ties/no ties.
- If you are making a table for interior elevated slabs you would normally be using 0.75" cover, do you therefore build into your table a change in equations after #6 bars, i.e. when the cover of 0.75" becomes smaller than 1 db?
- Similar questions for walls: at basement walls we show the vertical reinforcing as the outer curtain, but on shearwalls we show it inside the the horizontals - do you create two tables and account for the different typical covers for those two situations and then build that into your table? There is also the issue that portions of shearwalls may be tied/confined bars while others are not, this also may impact the development length.