Penpendrum
Civil/Environmental
- Sep 30, 2012
- 48
Hello everyone. . .
can anybody please clear me out the purpose of only splicing half of the reinforcement in one section and the other half in other sections for columns.. i have been told that this would somehow prevent congestion.. but is it stated in the ACI 318-11 commentary and in what section? I have been discussed in my previous thread that class B splices does not need to be staggered.. but why is it the inspector in the site won't allow me to splice all bars in one location. . the column dimension is 610x610 mm with 12-25mm DRB , 435x435 mm with 12-25 mm DRB , 585x585 mm with 12-25 mm DRB. .
the inspector showed me book (Design of Reinforced concrete by Jack C. McCormac * James K. Nelson) on Page 209 states that "Splices should be located away from points of maximum tensile stress, Furthermore, not all of the bars should be spliced at the same location- that is, splices should be staggered". .
the book was also based on ACI and it got me in a confusion that the statement above is in conflict the class B splice defined in the ACI code. .
please help me out . . I could loss a lot of money if He would demand to redo the work. ...thanks.
can anybody please clear me out the purpose of only splicing half of the reinforcement in one section and the other half in other sections for columns.. i have been told that this would somehow prevent congestion.. but is it stated in the ACI 318-11 commentary and in what section? I have been discussed in my previous thread that class B splices does not need to be staggered.. but why is it the inspector in the site won't allow me to splice all bars in one location. . the column dimension is 610x610 mm with 12-25mm DRB , 435x435 mm with 12-25 mm DRB , 585x585 mm with 12-25 mm DRB. .
the inspector showed me book (Design of Reinforced concrete by Jack C. McCormac * James K. Nelson) on Page 209 states that "Splices should be located away from points of maximum tensile stress, Furthermore, not all of the bars should be spliced at the same location- that is, splices should be staggered". .
the book was also based on ACI and it got me in a confusion that the statement above is in conflict the class B splice defined in the ACI code. .
please help me out . . I could loss a lot of money if He would demand to redo the work. ...thanks.