I didn't see where the OP said anything about the voltage level of the equipment under consideration...and where I work that has a profound effect on what steps are taken to prevent out-of-phase re-synchronization.
Here are some bare-bones descriptions, starting at the bottom and working up:
Our 4 kV distribution connected customers are required to have local loss-of-connection schemes to remove themselves from service, whether this be frequency excursion, under/overvoltage, overcurrent, or whatever. Typically, no communication paths of any kind are employed to provide remote tripping of the generator for feeder faults, although there are, of course, exceptions [there are ALWAYS exceptions]. Also typically, customer generation re-synchronization is prevented by supervisory schemes that block re-connection until stable voltage and frequency have been present at the customer site for a minimum of five minutes.
The connectivity confirmation of distribution-connected generators on our 13.8 / 27.6 / 44 kV networks is commonly provided by means of bi-directional comm paths, such that operation of a feeder breaker for any reason sends a trip signal to the generator's circuit breaker to open it, disconnecting the generator from the feeder; feeder circuit breaker reclosure back at the transformer station is supervised by receipt of a "distributed generator end open" [DGEO] signal from that customer...and if there are multiple distributed generators on the feeder, DGEO signals must be received from all of them before reclosure is permitted.
At 115 kV and up, the schemes can become quite sophisticated, but can also be all over the map; communication paths for remote/transfer tripping are generally, but not always, provided, and where they are not, almost invariably no breaker reclosure is even provided for the circuit breakers at the generating facility's terminal of that circuit; instead, that terminal of the circuit will be re-loaded by manual closure of breakers under the supervision of a synchro-check relay. Sometimes reclosure schemes are provided but are normally in the blocked state, their enabling being reserved for such occasions as planned outages where, due to station configuration, prompt re-energization of load-only equipment is feasible and desirable.
CR
"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]