Reclosing on BAAH/DB schemes 2

Status
Not open for further replies.

Sn00ze

Electrical
Jan 16, 2013
176
Is there any books,articles or standards I can look at with regards with reclosing schemes for Breaker and a half or dual breaker applications?
My system is 240kV (North America) with A/B line protections. A doing the reclosing on each of 3 lines on a ring bus dual bus. Each breaker is 1-pole trip/close.

Wondering what are the benefits/IEEE standards etc of reclosing 1 breaker (bus side) vs reclosing both (dual breaker).

Also, if you'd like to discuss based on your own experience, that would also be helpful.

Thank you.
 
Replies continue below

Recommended for you

one breaker only-Simplicity of automation. Closing the second breaker via SCADA is easy for a dispatcher.
static lead/follow-No dispatcher interaction required to restore the system
dynamic lead/follow breaker selection-Most likely to automatically close, and most complicated to automate.

What is a ring bus dual bus?
 
There is an IEEE standard that discusses Auto reclose schemes and is quite exhaustive. You may like to refer:
IEEE C37.104-2012 - IEEE Guide for Automatic Reclosing of Circuit Breakers for AC Distribution and Transmission Lines
 