recomendations after over speed event

Status
Not open for further replies.

byrdj

Mechanical
May 21, 2003
1,663
would you roll a STG unit (10MW air cooled) that exceeded 150% speed with out opening it up and inspecting.
 
Replies continue below

Recommended for you

Byrdj,

Before deciding on inspection, there are some factors that would definitely warrant opening the unit:

1. Was the coast down time normal?
2. Did the turning gear engage and the unit cooled down nomally? Abnormal vibrations during coastdown?
3. Is the shaft free to turn with no binding or strange noises?
4. Any debris found in the oil?
5. Any debris found in the exhaust?
6. Any opportunity to inspect the last stages without opening?
7. Any opportunity to borescope?

Depending on the criticality and downtime cost i would first exhaust all alternatives to do an educated assessment.
If the manufacturer's recommendations are that after such event the unit shall be opened and inspected then there is no room for argument. But if the instructions are silent or it is at the operator's discretion, I would try to avoid fixing something that is not broken.

What do yo think?


saludos.
a.
 
Thanks for the reply

I was not involved in the event. so I can't answer
But the main concern was to set the valves and try again

I just declined to assist and wonder if I'm too concerned.

I recall that 15% above OST was where things started to give on utility size units

hey, 30 years with out being at a "blow up" and don't want to ever
 
10MW is much smaller than the machines my experience is on, but my gut feel is 'no, I wouldn't roll it without inspection'. The manufacturer is the best one to make the call. My guess is that they would play safe and require inspection.

To add to Tick's list, were there any concerning vibrations during the overspeed event? Did it spend any time in a resonance range? How long was the duration of the overspeed?


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Thanks for your gut feel. (Mine too) In fact I'm surprised the unit stayed together.

Since my decline to assist, I doubt I will hear any more from them
 
Sometimes the decision is already made, the folk in charge just want someone to point the finger at if things go wrong. Under those circumstances I think you absolutely did the right thing by refusing to lend credence to what sounds like a pretty reckless plan.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
Before restarting the unit, it would seem sensible to:
- Figure out what caused the overspeed event in the first place.
- Figure out what automatic controls failed to stop the unit before it got much above 100pct, and fix them.




Mike Halloran
Pembroke Pines, FL, USA
 
Mike, that was sort of what I was going for. except I don't think I was suppose to hear about the runaway
 
I'll second the inspection. Run lubricants through lab too.
 
I suggest you write down a 'contemporaneous account' of whatever information exchanges you had about the overspeed event, and keep it for a long time. It smells like the kind of thing that eventually, inevitably, ends up in court, because of the amount of money involved.

E.g.: For the Diesels that my outfit sells, a single overspeed event ends your warranty. Period. Not negotiable. End of discussion.

Perhaps the STG manufacturer has a similar policy about overspeed events, in which case the perpetrators have career incentives to sweep such events under the rug, and to find someone else to throw under the bus when it arrives.




Mike Halloran
Pembroke Pines, FL, USA
 
Most of this conversation has been about the STG but I'd also be concerned about the generator especially if it is a 2 pole machine with retaining rings. At that speed the forces on the retaining rings and rotor slot wedges would have been tremendous. Better to have a look.

rmw
 
Thnks rmw. the generator would be my major concern too. 2pole air cooled w/rings

I think you might gather my question for recomendations following event was not for the excellent confirmations of items to inspected, but as a self check for me since it seemed I was the only one concerned. Since I've declined to assist, Im pretty sure I will not hear from them what they do one way or the other
 
ByrdJ,

I concur with your decision.

Sometimes a man has to do what a man has to do. You gotta live with yourself. If one of those retaining rings comes unglued and shreds the generator, at least it won't be on your watch. It looks like they had their minds made up but needed a scapegoat in case they were wrong.

rmw

PS: I assume you are a man.
 
That's a real bad sequence of events byrdj. Pretty much everything which could go wrong did so. Here's another one, in India this time:



----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
It's .pdf file - seems to have lost the file extension. Sorry.


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
150% overspeed! Wow! Didn't the machine have a trip governor to interrupt the steam supply at the turbine? I've never seen even very small steam turbines without one.

I agree with previously stated concerns that the generator is a greater issue--air-cooled generators can catch fire quite readily.

You certainly were wise to stay clear of that obvious set-up. Any short-term compensation would almost certainly have been quickly overshadowed by less than pleasant events.
 