The following information is from:
Water Supply
Proper operation of emergency equipment requires the availability of a large and continuous supply of potable water. The water supply must, at a minimum, be capable of delivering the volumes of water required by the ANSI standard. Piping should be at least as large as the inlet size of the unit to be installed. The water supply line must also be capable of delivering an uninterruptible flow of water of at least 30 PSI flow pressure.
Water Temperature
The ANSI standard provides that the water delivered by emergency equipment be “tepid” (that is, moderately warm or lukewarm). Tepid water is generally defined as between 60 and 100 degrees Fahrenheit. However, where it is possible that a chemical reaction might be accelerated by warm water, a medical professional should be consulted to determine what the optimum water temperature would be.
The delivery of tepid water to emergency equipment may raise complicated engineering issues. In geographical areas subject to cold weather, the water supplied by public water systems can be quite cold, at times just above freezing. Providing tepid water requires heating the cold water or blending it with hot water to achieve a desirable temperature. Conversely, in warm areas of the country, water standing in pipelines can be heated to a very hot temperature. Providing tempered water would then involve chilling the water or adding cold water to the water supply line.
There are several ways to design a water supply system to address the tepid water requirement. First, it is possible to provide both hot and cold water supply lines to each location at which emergency equipment is installed. This is typically done in facilities (such as laboratory buildings and schools) where hot and cold water systems are installed throughout the building. At each emergency unit, a tempering valve would be installed to blend the hot and cold water to a preset temperature. The tempering valve must be specially designed for use with emergency equipment, since these valves have dual built-in safety features. In the event that there is an interruption in the hot water supply, the valve will still deliver a full flow of cold water to the equipment. If there is an interruption in the cold water supply, the valve will shut off the water entirely to eliminate the possibility of scalding. Please refer to the “Tempering Units” section of this catalog for information on Guardian tempering valves.
The second way to address the tepid water issue is to install a recirculating tepid water system. This system can supply multiple emergency equipment stations. The system continually recirculates warm water to each location. If one or more units are activated, the system will automatically blend hot and cold water and add it to the water line to supply the units. These systems must be sized and engineered for the particular facility in which they are to be installed. It is therefore common to consult with the emergency equipment manufacturer during the design process. Please contact our regional sales representatives or the factory for information on recirculating tempered water systems.
I hope this helps