Recover cooling energy from Nitrogen Vapour Exhaust / Air mix

Status
Not open for further replies.

joegrey

Mechanical
Jan 16, 2012
1
Does anyone know of a way to recover the cooling energy from a liquid nitrogen vapour / air mix coming out of a Liquid Nitrogen freezing process? The vapour mix is at -80F and flowing at 3000 CFM. Snow flakes are generated at the fan exit on the roof from the moisture in the air from the process room. A dual exhaust fan set-up is being used because the stainless squirl cage fans do freeze up occasionally.
Goal is to transfer some of this cooling energy to cool an existing room.
 
Replies continue below

Recommended for you

You could do it with a multipass heat exchanger.
A single pass exchanger would leave you with a block of ice on the warm side.
B.E.

The good engineer does not need to memorize every formula; he just needs to know where he can find them when he needs them. Old professor
 
how about drawing some of the air at -80 off and mixing with some ambient air to get it to a reasonable temp then run it through a heat exchanger into your system?
 