Hi All,
IEEE red book says that a high resistance grouding is not recommended on systems at 15 KV because it requires a very sophisticated relaying. That measn NGR should be set to have a ground fault current of 100 A or more.
In todays's world where Digital relays are a trend, Do you guys still agree?
We have a 10 MVA 69 KV/ 13.8 KV system and conductors are taken to a shaft unedrground, because of 100 A, NGR current value, the drop in the grounding conductor which will act as a ground potential rise for an equipment inside the mine, we have to limite the value of NGR current.
So when we decided to reduce to 50 A, the Red book argument came flying...
Kindly advise.
Thanks