My team is working a project where the concrete contractor misaligned a few cast-in place anchors. We need to remedy this by replacing the cast-in place anchors with threaded rod epoxy anchors. The issue we're having is that the column base plates do not allow us to meet the required anchor spacing for epoxy anchors.
Required spacing between anchors = 3-3/4"
Actual spacing between anchors = 3"
I have spoke with HILTI engineers to see if they have any literature for a reduction in strength based on a reduced anchor spacing, they do not. Tapcon allows for said strength reductions based on reduced spacings, our thought was to use a similar reduction factor to justify the use of the epoxy anchors we're trying to use.
Looking to get other professional opinions on this or any alternative ideas on how to combat this anchors spacing issue.
Thanks.
Required spacing between anchors = 3-3/4"
Actual spacing between anchors = 3"
I have spoke with HILTI engineers to see if they have any literature for a reduction in strength based on a reduced anchor spacing, they do not. Tapcon allows for said strength reductions based on reduced spacings, our thought was to use a similar reduction factor to justify the use of the epoxy anchors we're trying to use.
Looking to get other professional opinions on this or any alternative ideas on how to combat this anchors spacing issue.