Redundancy aspects for District Cooling system

Status
Not open for further replies.

SDTH

Mechanical
Mar 4, 2017
19
Hello all,
Is there any international standard (ASHRAE/IDEA) OR any local regulatory authority which specifies to have redundancy for Chillers of District cooling plants?
If so, how much is the % redundancy?
If not, what is the standard industrial practice?
Thanks in advance,


SDTH
 
Replies continue below

Recommended for you

Define your district cooling plant first.

It is common practice to be 100% redundant for maintenance if nothing else.

 
I don't think a JHA cares unless you cool something that in itself is required by code. It is more up to the owner/operator what they need and feel comfortable with. Maybe some cooled buildings are not mission-critical, maybe everything is.
Chiller plant design is more than N+1. You may have different size chillers etc.
 