Two DC PS units connected in parallel through blocking diodes. Two diodes or four diodes?
Thanks
 
Replies continue below

Recommended for you

two, as shown below

29wp9wg.jpg


or you can buy a DIN rail mount 'isolator' with heat sinks ans wiring terminals:

29ym3d3.jpg
 
Thanks Danw2
I always have been using this configuration but recently I found circuits with blocking diodes at positive and negative ends of each PS.
Do you know the reason? I think that depending upon the event of specific earth faults an overvoltage (2 times Vn) could be applied to the load. Is this a correct assumption?
 