  • Congratulations IRstuff on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!
Redwood beam bending stress
m1208
71
I have an exterior second story wood deck and need to replace the existing 6x12 (22' long) wood beam. I like to use redwood beam to prevent dry rot issues. The only available beam type in our area is 6x12 redwood, con-heart grade. For design, I need the allowable bending stress for the 6x12 redwood beam. The Codes (i.e. NDS and UBC) do not have the bending stress listed for members thicker than 4" (see attachment). Any idea where I can get allowable bending stress for 6x12 redwood beam. If nothing is listed then I have to use glued-laminated beam, and in that case, how do I make sure that the beam is rated for weather exposed area?
  • CCF05282025_0001.pdf
Why not use a pressure treated beam? Or if that doesn't calc you would likely want an Alaskan cedar glulam for exterior rating or you could use a wolmanized PSL (Weyerhauser) or treated LVL (Pacific Woodtech)
I could not find 6x12 pressure treated in our area. Are there any listed bending stress values for pressure treated beam of 6x12? If we use glulam, how do we make sure that is for exterior use, subject to rain, when they deliver it to the job site?
NDS Supplement lists Redwood in Table 4D, Reference Design Values for Visually Graded Timbers (5"x5" and larger). There's a section in the table for "Beams and Stringers." But you can also check with the supplier to see under what rules the timber was graded and go to them for design values. It will also let you verify that it has actually been graded, which is important.
But yeah...don't just check stresses. Do a complete design. Deflection is going to be a serious issue with this. Unless the deck's only 4' deep. If it's carrying 2' of trib it might pass...maybe...
NDS supplement Table 4D lists Reference Design Values for Visually Graded Redwood Timbers (5"x5" and larger), but Con-Heart (Construction Heart) is not listed in the table as a commercial grade. I am not familiar with redwood, but a quick google search revealed one source that states that con-heart is not graded for strength. I suggest seeking documentation from the Redwood Inspection Service (RIS, grading agency for redwood) for additional information about available grades and the intended usage of available grades, but the short answer to your question about reference design values is of course they are available for redwood beams
