warmulli
Electrical
- Feb 9, 2011
- 8
I have come across a REF setup causing some confusion, any help. Comments are welcome!
Setup: One 11KVA transformer with two LV feeds supply two C&H LV Switch panels with one switch panel containing a interconnector supply another LV panel.
The MCAG setup is as follows: MCAG relay located on the main LV Switch panel with CT's installed on both LV switch panels protecting the supply cable with no CT's installed on the Sub panel as this is fed via the interconnector.
This is where the confusion starts, On the LV switch panel with the MCAG relay fitted there was 4 CT's installed 800/5 ratio main incomer ACB rated at 800Amps, on the other switch panel there was 3 CT's installed ratio 1600/5, Main incomer ACB rated at 1600amp, missing the Neutral CT causing the relay to trip when the load become unbalanced due to the missing Neutral CT not be able to observe the Neutral current. This was rectified by installing the missing Neutral CT. The arguments is some people are saying that the ratio of the CT's at both panels have to be the same ratio and that the 800 CT's will need to be changed for 1600 CT's for the correct operation of the MCAG relay. My understanding is as long as the set of 4 CT's are matched then there is no need to swap the 800 for 1600. By changing out for 1600 ratio CT's your reducing the required fault current needed to trip the relay.
Upon viewing the as built drawings the above setup is as per drawing including the missing Neutral CT, there is also a N-Earth link missing on one of the LV panels. The panels are around 12 years old and as being cutler and Hammer there is no way of getting any information out of them.
Setup: One 11KVA transformer with two LV feeds supply two C&H LV Switch panels with one switch panel containing a interconnector supply another LV panel.
The MCAG setup is as follows: MCAG relay located on the main LV Switch panel with CT's installed on both LV switch panels protecting the supply cable with no CT's installed on the Sub panel as this is fed via the interconnector.
This is where the confusion starts, On the LV switch panel with the MCAG relay fitted there was 4 CT's installed 800/5 ratio main incomer ACB rated at 800Amps, on the other switch panel there was 3 CT's installed ratio 1600/5, Main incomer ACB rated at 1600amp, missing the Neutral CT causing the relay to trip when the load become unbalanced due to the missing Neutral CT not be able to observe the Neutral current. This was rectified by installing the missing Neutral CT. The arguments is some people are saying that the ratio of the CT's at both panels have to be the same ratio and that the 800 CT's will need to be changed for 1600 CT's for the correct operation of the MCAG relay. My understanding is as long as the set of 4 CT's are matched then there is no need to swap the 800 for 1600. By changing out for 1600 ratio CT's your reducing the required fault current needed to trip the relay.
Upon viewing the as built drawings the above setup is as per drawing including the missing Neutral CT, there is also a N-Earth link missing on one of the LV panels. The panels are around 12 years old and as being cutler and Hammer there is no way of getting any information out of them.