HI,everybody.
I have a 90MVA 330/132/13.8KV Yyd transformer that always trips on REF due to an earth fault on the 330KV line,and is very stable during normal loading.
I have sometime ago carried magnetisation test on all CTS and discovered that the ones on the Neutral bushings were of the X- class whereas the external ones are of protection class,and thus have the ones on the bushings replaced with protection types.The CT ratios on primary is 150/1A, and 400/1A on the secondary,and is always the secondary REF relay that flags.Can anyone think of a solution please.
I have a 90MVA 330/132/13.8KV Yyd transformer that always trips on REF due to an earth fault on the 330KV line,and is very stable during normal loading.
I have sometime ago carried magnetisation test on all CTS and discovered that the ones on the Neutral bushings were of the X- class whereas the external ones are of protection class,and thus have the ones on the bushings replaced with protection types.The CT ratios on primary is 150/1A, and 400/1A on the secondary,and is always the secondary REF relay that flags.Can anyone think of a solution please.