Hello everyone.

I have some VRF heat pumps in a boiler room that contains R-410a. From my understanding of ASHRAE 15, I am ok if the boilers are direct vented. Otherwise I will need a refrigerant monitor to interlock with the boilers to prevent the open flame creating phosphene gas from burning leaked refrigerant.

I also have other smaller gas equipment in the room such as gas unit heaters and a duct furnace. Do all these other pieces of equipment also need to be direct vented or is there some kind of code exception?
 
Replies continue below

Recommended for you

In 2023, I don't understand why you would not use sealed combustion on all devices regardless of refrigerants. What makes you think a furnace is different from a boiler when it comes to the flame and refrigerant?

Depending on the amount of refrigerant, you may need to install refrigerant monitoring and ventilation.

 