Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

refrigerant velocity

Status
Not open for further replies.

PaulLag

Mechanical
Jul 26, 2013
106
Hi there

hope everybody is fine !
Please, I am facing to following question.
Can anybody help me in order to determine which is the minimum refrigerant velocity we need to have in an heat exchanger in order to allow oil return to compressor ?
I am referring specifically to an evaporator.

I assume this will be function of evaporating temperature.

Please, can anybody give me an hint or suggest me some specific literature ?
thanks in advance !

 
Replies continue below

Recommended for you

The problem as a general rule is not in the evaporator coil/coils, they should be designed to allow the oil to drain by gravity to the suction tube.
However the suction line itself should be designed to get the oil from the evaporator to the compressor without slugging the oil. Suggested gas velocities are in the 500fpm range for horizontal lines, and in the 1500 fpm range for vertical up lines.
B.E.

You are judged not by what you know, but by what you can do.
 
 http://www.srcoils.com/2887wp/wp-content/uploads/2012/06/Evap-Coil-Primer.pdf
Status
Not open for further replies.

Part and Inventory Search

Sponsor