Hey all,
Sorry if this get long winded. More info is better than too little. I need some input on a little server room project. I am expanding my server room because it has just gotten TOO small. I have a typical IT department that feels the need to take up every last availble space in the rack with "another blade or switch" and if the room can fit two racks then let's stick another rack in the room....fill it with blades and switches...blah, blah. My air flow is now non-existing and my mini split is satifying the room temp of 68 but not neccessarily keeping the servers as cool during peak usage.
Original layout of the room is 6' x 10' x 8' high. I installed a 21,500 BTU mini split at 7' for the single 6' rack. Over the years an addional 6' rack and computer station was placed in the room. The existing mini split system still maintains the room temp but with the air flow pattern non-existing we've had to add box fans to create an adquate air pattern. Per HP, Dell, APC etc the total BTU output (once you add up their calculations) is 90,000 BTU!! There is no way my server room need or could handle an 8 ton unit.
Now, for the feedback.
I'm going to elongate the room and add a new primary cooling system but leave the existing mini split as my back-up or supplemental system. I feel that a walk-in type ceiling mounted fan coil would be best because they draw from the back and exhaust cool to the front. I can place it towards the rear of the racks (heat load) and exhaust cool air above the racks and cycle off the wall back into the servers. Since my new server room will basically be longer than wide I will be creating a cold front portion and a warm back portion. The air flow pattern is ideal. Since the walk-in fan coil is 3-4 times the CFM of my A/C fan coil I figure I can maintain or drop my BTU rating of the coil (compared to an A/C coil) and then size comdensor unit. My thought process was to basically to create an over capacity wine cooler.
Here is what I plan to mesh together; Tecumseh 1 hp R135A AJA4512 Condensing unit (interior-place in warehouse) with a Bohn 9000 BTU, 1300 CFM electric defrost (should never need). I'll use a pressure switch and TXV instead of a thermostat. So, what am I missing or over looking?
Rip away...
Sorry if this get long winded. More info is better than too little. I need some input on a little server room project. I am expanding my server room because it has just gotten TOO small. I have a typical IT department that feels the need to take up every last availble space in the rack with "another blade or switch" and if the room can fit two racks then let's stick another rack in the room....fill it with blades and switches...blah, blah. My air flow is now non-existing and my mini split is satifying the room temp of 68 but not neccessarily keeping the servers as cool during peak usage.
Original layout of the room is 6' x 10' x 8' high. I installed a 21,500 BTU mini split at 7' for the single 6' rack. Over the years an addional 6' rack and computer station was placed in the room. The existing mini split system still maintains the room temp but with the air flow pattern non-existing we've had to add box fans to create an adquate air pattern. Per HP, Dell, APC etc the total BTU output (once you add up their calculations) is 90,000 BTU!! There is no way my server room need or could handle an 8 ton unit.
Now, for the feedback.
I'm going to elongate the room and add a new primary cooling system but leave the existing mini split as my back-up or supplemental system. I feel that a walk-in type ceiling mounted fan coil would be best because they draw from the back and exhaust cool to the front. I can place it towards the rear of the racks (heat load) and exhaust cool air above the racks and cycle off the wall back into the servers. Since my new server room will basically be longer than wide I will be creating a cold front portion and a warm back portion. The air flow pattern is ideal. Since the walk-in fan coil is 3-4 times the CFM of my A/C fan coil I figure I can maintain or drop my BTU rating of the coil (compared to an A/C coil) and then size comdensor unit. My thought process was to basically to create an over capacity wine cooler.
Here is what I plan to mesh together; Tecumseh 1 hp R135A AJA4512 Condensing unit (interior-place in warehouse) with a Bohn 9000 BTU, 1300 CFM electric defrost (should never need). I'll use a pressure switch and TXV instead of a thermostat. So, what am I missing or over looking?
Rip away...