Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Refrigeration reheat inquiring

Status
Not open for further replies.

cme

Mechanical
Jan 16, 2003
196
I have a project involving a 70 ton rooftop MAU seving a science lab. 100% OSA.

Basis of design is around AAON with a modulating hot gas reheat coil / scheme.

I'm looking at McQuay RPS model and their reheat scheme is via a subcooling coil between the condenser and TXV.

Would welcome your input / experiences with these units and or schemes.
 
Replies continue below

Recommended for you

I cannot speak to your specific unit, but I have had nasty problems with other McQuay equipment using waste heat as reheat. My personal preference is to keep the refrigeration components as uncomplicated as possible. You are generally looking at high dollar equipment with the compressors, and refrigerant leaks can be a huge maintenance issue.

It's possible that if it's all self-contained in a unitary rooftop, that may minimize the potential problems. Nevertheless, caution is advised.
 
In supermarkets it is common to use the hot gas discharge from the compressors to operate a reheat coil.

I'm not sure how much heat would be available if the refrigerant has already gone through the condenser. It seems like your coil size (and air pressure drop) would be less if you used the hottest fluid. Don't know what refrigerant you are using.

Getting it factory piped would be great. Anything done in the field may be lacking quality.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor