Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Reheat VAV for hospitals

Status
Not open for further replies.

cctrk

Mechanical
Mar 15, 2001
21
I am looking for advantages of reheat type VAV for hospitals.

How shall it be applied correctly especially for patient wards?
 
Replies continue below

Recommended for you

In fact fcu, can it be compared?
 
I think you need to narrow it down to what type of patient room it is; long term, domiciliary, or nursing hoome has different requirements than general in-patient. The ASHRAE HVAC Design Manual for Hospitals and Clinics recommends no wet coil inside the room for inpatient, all environment control by air side. For nursing home/domiciliary, you can drop room air changes from 6 to 4 is using supplemental heat. If the outside air is through a fcu, then O&M bill goes up. If the OA is through the AHU, then you need to provide all ACH from the DOAS. I'd prefer (and am doing now) to put 4 ACH through a DOAS and use an energy recovery wheel, especially when the facility includes bed pan washers. That seems to please the infection control people and is acceptable to the energy engineer (at least here).
For a large hospital, then need for perimeter heating/cooling becomes an issue, and a fcu has advantages.
 
Filtration requirements of 85% for most hospitals eliminate the FCU system.
If rooms are used isolation room etc. re-circulation is not allowed.
Check the healthcare deisgn guideline.
Not many hospitals are done using FCU's.

Stick with VAV
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor