Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

reinforcing bar positioner requirement

Status
Not open for further replies.

inspjerry

Structural
Jan 26, 2005
7
I keep hearing reinforcing bar positioners for masonry mentioned in the ACI 350, but cannot find them anywhere,and I am unable to find any refrence to them in the new 2003 IBC. Anyone tell me where the requirement is?
 
Replies continue below

Recommended for you

ACI 530.1 Section 3.4 states that rebar shall be secured as to "prevent displacement beyond the tolerances allowed". The corresponding commentary section shows some typical rebar positioners. I don't see where a spacing requirement is given, but we specify a maximum spacing of 200 bar diameters.
 
Yes, but the new 2003 IBC states somewhere 112 bar diameters.
 