I am a project manager on a waterwater treatment project and the inspector (construction manager in this case) and myself have had some issues over rebar clearence. He thinks more clearance is better.
e.g. On Mat slabs, the inspector instructed us to shorten the rebar standees height to create more top and bottom clearence. His comment more clearence is better (i.e. corrosion concerns). I informed him he better check with the structural designer since this affects the streight of the slab.
After convincing him he was wrong he started enforcing CRSI tolerance of +/- 1/2". I accepted this tolerance for all area except the bottom mat cast against earth.
We requested a bottom mat of clearence of +1/2" to -1 1/2". I aurgued the grade is irregular and that is why you start with a 3" clearance so that you can get a minimum of 1 1/2" clearance. I asked them to run this by the designer.
He will not run my request by the designer since he has a code (CRSI) that says +/- 1/2". He is a by the book inspector with no common sense.
For you information the reason we are having trouble getting a level plan of 3" clearance is the following:
The rodbuster foot traffic slightly shifts the gravel subbase that was level and tested prior to instalation of reinforcing steel.
The rod buster burys a bar (every 4th bar) so you natually get less clearance under those bars. At one point, the inspector has suggested we should hand excavate a trough under the bury bars.
The rebar supports (we are using 8" x 8" bricks) are actually only 2 3/8" high and do sink in the gravel a little (1/2" to 3/4"), but the 2 3/8" works well since the rodbuster is burying a #6 bar. This get the majority of the bars at the right plane (3" above grade).
So my question is: Should the CRSI tolerance of +/-1/2" for rebar clearance apply to the bottom mat cast against earth or does the design standard of 3" allow for a greater variance.
e.g. On Mat slabs, the inspector instructed us to shorten the rebar standees height to create more top and bottom clearence. His comment more clearence is better (i.e. corrosion concerns). I informed him he better check with the structural designer since this affects the streight of the slab.
After convincing him he was wrong he started enforcing CRSI tolerance of +/- 1/2". I accepted this tolerance for all area except the bottom mat cast against earth.
We requested a bottom mat of clearence of +1/2" to -1 1/2". I aurgued the grade is irregular and that is why you start with a 3" clearance so that you can get a minimum of 1 1/2" clearance. I asked them to run this by the designer.
He will not run my request by the designer since he has a code (CRSI) that says +/- 1/2". He is a by the book inspector with no common sense.
For you information the reason we are having trouble getting a level plan of 3" clearance is the following:
The rodbuster foot traffic slightly shifts the gravel subbase that was level and tested prior to instalation of reinforcing steel.
The rod buster burys a bar (every 4th bar) so you natually get less clearance under those bars. At one point, the inspector has suggested we should hand excavate a trough under the bury bars.
The rebar supports (we are using 8" x 8" bricks) are actually only 2 3/8" high and do sink in the gravel a little (1/2" to 3/4"), but the 2 3/8" works well since the rodbuster is burying a #6 bar. This get the majority of the bars at the right plane (3" above grade).
So my question is: Should the CRSI tolerance of +/-1/2" for rebar clearance apply to the bottom mat cast against earth or does the design standard of 3" allow for a greater variance.