charz
Electrical
- Jan 11, 2011
- 95
The relay name plate mentions the following,
Making Capacity: 10A
Breaking Capacity: 2A
There is no continuous current rating mentioned.
I have my load operating continuously at 4A. Would be there any problem breaking this current of 4A? If so, the continuous current carrying capacity of the load should be less than or equal to breaking capacity in general?