jhonsom
Electrical
- Nov 13, 2009
- 32
1. Which Relay is the best for detecting fault in high impedance grounded/ungrounded multiple synchronous generators in parallel?
What I think is voltage based ground fault detection is not very sensitive/selective for this type of ground. 59G, 64G (VN, VN3) are all good as backup protection only.
67G uses I0 and 3V0 where I0 is math calulated from 3 phase CT and 3V0 math calulated from 3 phase PT (broken delta not used).
67N uses IN and 3V0 . I think 67N should be the primary protection.
we currently have only 1A,5A nominal CT's, thinking of including 50mA,0.2A CT's to be more sensitive for this type of grounding.
2. Also is it required to add 67N funtion for this type of grounding in distribution feeder relay?
Please share your experience/opinion on this.